We have a new parking garage we're working on and it's calling for T5 Fluorescent fixtures. The panel schedule and fixture schedule says they should be 208v on a 2 pole breaker? Has anyone ever installed these type of fixtures? I've only installed 120v and 277v? I didn't know there was a 2 pole 208v T5 fluorescent fixture? Any input would be helpful.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Welcome to the forum.

Most all electronic ballasts are universal voltage and will work on 120V to 277V and every voltage in between. I don't know why your project specs 208V other than a way to reduce voltage drop which would not be a real problem if MWBC's were used.
 