C cyriousn Senior Member Location ME / CT Occupation EE & BIM Feb 2, 2011 #1 What is an example of the effective insulation refered to in condition 1 of table 110.26(A)(1)? Thanks!
What is an example of the effective insulation refered to in condition 1 of table 110.26(A)(1)? Thanks!
chris kennedy Senior Member Location Miami Fla. Occupation 60 yr old tool twisting electrician Feb 2, 2011 #2 Drywall.
C cyriousn Senior Member Location ME / CT Occupation EE & BIM Feb 2, 2011 #3 I guess i was overthinking it. Seems like they are just refering to is the wall material.
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Feb 2, 2011 #4 I once put on a drawing that a handrail (located between 36 and 42 inches from a panel on the opposite side of a catwalk, with the panel rated 220/380V) had to be wrapped with a rubber material, so that I could call it a Condition 1 installation.
I once put on a drawing that a handrail (located between 36 and 42 inches from a panel on the opposite side of a catwalk, with the panel rated 220/380V) had to be wrapped with a rubber material, so that I could call it a Condition 1 installation.