Based on table 210.24 I can tap a 20Amp circuit with a 14 AWG??

example: 14AWG pigtails on 20Amp receptacle outlet circuit, 14 AWG switch leg for a 20A rated garbage disposer circuit
 

Smart $

Esteemed Member
Location
Ohio
2011 NEC
Based on table 210.24 I can tap a 20Amp circuit with a 14 AWG??

example: 14AWG pigtails on 20Amp receptacle outlet circuit, 14 AWG switch leg for a 20A rated garbage disposer circuit
Only if the tap complies with 210.19(A)(4) Exception No. 1...

...which is to say no to your examples.
 