2011 NEC
Based on table 210.24 I can tap a 20Amp circuit with a 14 AWG??
example: 14AWG pigtails on 20Amp receptacle outlet circuit, 14 AWG switch leg for a 20A rated garbage disposer circuit
Not in those examples. That #14 is still branch circuit wiring.
Only if the tap complies with 210.19(A)(4) Exception No. 1...2011 NEC
Based on table 210.24 I can tap a 20Amp circuit with a 14 AWG??
example: 14AWG pigtails on 20Amp receptacle outlet circuit, 14 AWG switch leg for a 20A rated garbage disposer circuit
See 210.19(A)(4) Exception No. 1.Why is there a tap 14 awg under the 20A circuit? When can that be used?