I was turned down on a wall rough in house remodel for using a 14-3 switch leg for a ceiling fan that is fed off a 20 amp recp. circuit. I was using table 210.24, according to this table, minmum size condutor for a 20 amp circuit is #12 and taps can be #14 awg. The Inspector said do not tie #14 wire to #12 wire. AM I missing something?