Table 220.42 table 220.44

Status
Not open for further replies.

Djelite

Senior Member
Location
Ny
Occupation
Electrician
Table 220.42 is used for dwelling lighting load demand factor which also in includes receptacle@3va per sq.ft. Hospital hotels and warehouses are also listed here. Yet table 220.44 is used for demand for for other than dwellings. Whats the difference between the two table for other than dwelling?
 
220.14(J) for Dwellings list the outlets that can be included in the General Lightind and subject to 220.42. Other than Dwellings only the lighting loads are covered by 220.42
 