Table 220.55

Status
Not open for further replies.

Tainted

Senior Member
Location
New York
Occupation
Engineer (PE)
For me table 220.55 has always been the hardest to grasp in article 220

There is an oven rated 2200kw
and a cook top rated 11500kw

What is the demand load? I am getting 11kw is this correct?
 
If I recall you can add the watts of one oven and one cooktop and use column C and treat it as one range.

That would mean 1 unit at 14kw but I believe you can also do them separately using col A and C
 
Average the two using 12 as the smallest number...gives you an average of 17.... 5% for each kw over 12... If I did the math correct = 14
 
Look at Example D6B in Annex D (Pg 799 in '17)
I still don't get it. Note #4... This is for branch circuit but I assume it would be the same for the demand load

The example you showed was for ranges only. You are dealing with averages here we are not just using Note #4
 
If someone thinks note #4 doesn't apply for demand load then you would have to use each one individually. The 11.5 kw = 12 kw = 8kw demand from table

2.2 kw *80% = 1.76 =

8kw + 1.76 Kw = 9.76= 10 kw
 
If someone thinks note #4 doesn't apply for demand load then you would have to use each one individually. The 11.5 kw = 12 kw = 8kw demand from table

2.2 kw *80% = 1.76 =

8kw + 1.76 Kw = 9.76= 10 kw
I'm confused now, is the answer 8800W or 10000W lol
 
I'm confused now, is the answer 8800W or 10000W lol
IMO... it 8.8

If this is for a test I believe 8.8 is the answer. The 10kw is another way to calculate it. Using Note 4 I see the answer as 8.8

If you have 2 units- cooktop and oven they can be added together. Let's face it a range is nothing but a cooktop and an oven. I would just ignore the 10kw it complicates things and wasn't necessary.
 