GerryB
Senior Member
- Location
- woodbridge, ct. USA
I am looking at some drawings for some pretty long wire runs underground in 2" pvc. I think they have oversized the grounds, for ex. A 240 volt single phase, 60 amp load at 400 feet. The drawings have 3-1/0 conductors and a #2 ground. I think you could use a #1 conductor, but according to the table, #1 or 1/0 would it not be a #6 ground?