When using Table 250.102(C)(1), and using parallel feeders I am interpreting note 3 to say to add the kcmils of each parallel to get the size to use for sizing the size of the grounded conductor.
3. If multiple sets of service-entrance conductors are used as permitted in 230.40, Exception No. 2, or if
multiple sets of ungrounded supply conductors are installed for a separately derived system, the equivalent
size of the largest ungrounded supply conductor(s) shall be determined by the largest sum of the areas of the
corresponding conductors of each set.
We are having a discussion with an engineer that thinks you only need to use one of the parallels to do the sizing.
Example: Parallel 500kcmil 2 sets would be 1000kcmil and would size the grounded conductor at 2/0 CU or 4/0 AL.
The engineer stated that it should be sized at #2 CU or 1/0 AL.
I know that you should add the parallel sets together, I am looking for confirmation.