- Occupation
- Licensed Electrician
There is nothing to add. You have two conduits with 500kcmil ungrounded conductors in each. 500kcmil in the first conduit requires a 1/0 min grounded conductor. 500kcmil in the second conduit requires the same.
It clearly says in the raceway.
If all of the parallel conductors where in a single wireway then you would add them, if they were in several separate raceways then you only need to use the size of the underground conductor in each raceway.
I'm as lost as tkb on this.
The size of the grounded conductor in each raceway or cable shall be based
on the total circular mil area of the parallel ungrounded conductors
in the raceway
There's two 500MCM conductors in each raceway totaling 1000MCM