Does the NEC say anything about the use of welding cable to permanent/ temporary wiring? is this permitted?
And if it is dual listed you still have to find terminals that are listed for fine stranded wire. They exist but are not easy to buy off the shelf.Unless this welding cable is dual listed as a conductor type found in article 400 it cannot be used for any NEC power installation.
The only dual listed welding cable that I have seen was listed as a type found in Article 310, not 400...it was listed RHH/RHW.Unless this welding cable is dual listed as a conductor type found in article 400 it cannot be used for any NEC power installation.
If you can get crimp type terminals that are listed for the cable and then bolt the connections to the device as a suggestion.And if it is dual listed you still have to find terminals that are listed for fine stranded wire. They exist but are not easy to buy off the shelf.
I have applied solder to fine strand cable and terminated it in a mechanical lug and walked away feeling that there would never be a issue. The cable is in service today....4/0 fine strand with about 150-200A on it. No issue no problem.
Im sure the code vultures will have issues though LOL
Excellent suggestion. I have done that in the past and think it is probably the best way.If you can get crimp type terminals that are listed for the cable and then bolt the connections to the device as a suggestion.
Yes, that is a cable that is covered by Article 400, but my comment was about dual listed "welding" cable. Type W power cable is not welding cable.I always used Art. 400 Type W for temp/generator cable. Used to buy a ton of it in 2/0 and 4/0 for this.
Assuming that the insulation has the correct voltage rating and you use terminations suitable for the fine strands, I don't see any real danger....just a code violation.I understand this would be a code violation but what are the possible dangers in using this welding cable with the generator?
Sent from my SM-G900H using Tapatalk