Should the proposal for 250.4 (A) 5 be "unsubstantiated", this revision would at least eliminate the risk of EGC fusing where disconnection times exceed 5 seconds. However, this will not solve or mitigate the danger of touch potential.
Table 250.122
Table 250.122
Size of Largest Ungrounded Conductor | Size of Circuit Protective Conductor | |
(AWG or kcmil) | (AWG or kcmil) | |
14 | 14 | |
12 | 12 | |
10 | 10 | |
8 | 8 | |
6 | 6 | |
4 | 6 | |
3 | 6 | |
2 | 4 | |
1 | 4 | |
1/0 | 3 | |
2/0 | 2 | |
3/0 | 1 | |
4/0 | 1/0 | |
250 | 2/0 | |
300 | 3/0 | |
350 | 3/0 | |
400 | 4/0 | |
500 | 250 | |
600 | 300 | |
700 | 350 | |
750 | 400 | |
800 | 400 | |
900 | 500 | |
1000 | 500 | |
1250 | 600 | |
1500 | 750 | |
1750 | 900 | |
2000 | 1000 | |