1793
Senior Member
- Location
- Louisville, Kentucky
- Occupation
- Inspector
I will be doing an Outdoor Residential Service Heavyup and I will be adding a few more circuits. My question is in line of derateing. I will have 6 circuits that will be MWBC and one standard for a total of 7 circuits. If I have 3 sets of MWBC the neutral, grounded conductor, for these circuits do not count as a CCC --- correct?
I?m installing #12 THHN/THWN in 3/4? EMT so fill is not an issue just want to be sure I have the ampacity I need for each 20 amp circuit.
I?m installing #12 THHN/THWN in 3/4? EMT so fill is not an issue just want to be sure I have the ampacity I need for each 20 amp circuit.