Bjenks said:
table 310.15(B)(6) and a new one for me is you can't use it unless it is carrying the full current of the dwelling unit.
That one caught me by suprise too.
In the past, I've used a combo 200A Meter Main to supply a 200A MLO panel inside the home.
I've always used 4/0 al for the feeder between the panels per 310.15(B)(6).
Sometimes, I would install a couple of 2 pole breakers in the Meter Main to supply the outside A/C compressors, if they were handy.
Under the new rule, I don't think that this is allowed.
Since the 4/0 feeder wouldn't be carrying 100% of the power to the dwelling...I can't use 310.15(B)(6).
The ironic thing is that I could use 310.15(B)(6)..... power all the circuits (A/C compressors included) from the MLO panel... and be in compliance, even though it would add the additional compressor load to the 4/0 al feeder.
So...in a nut shell...and in my humble opinion...if you plan on using 310.15(B)(6), there's no need to buy a Meter/Main with additional breaker space,
unless you're planning on powering a out building or other remote structure from the "free" breaker spaces.
If you sized your Main Power Feeder from 310.15(B)(6), the moment that you place a breaker in the Meter/Main to power a house circuit, you are technically non-compliant.
Just my opinion, and interested in hearing yours
steve