Well thanks for the great info I tried to pass it along. I contacted the supply house and they are baffled. They told me that they carry #2 CU and that good for dwelling service, feeders ect. at 100 amps. I told the owner it won't work code does not allow it. He tells me they don't stock the SE stuff as we only stock Copper wire no Aluminum. I said you can get the stuff in copper too. He's going to continue with the same. I guess I am out of luck unless I want a big roll. That is what I get for wanting to use copper.
I had a some #2 AL SE cable out back so I used it.
Your OP was asking about #4 now you mention #2. The ampacity of 2-3 CU NM is 95 amps so as long as the calculated load is 95 amps or less it can be used for the feeder and protected with a 100 amp breaker.
I don't know much about your area but I have worked in many parts of Northern CA and every supply house I have been to has stocked AL SE cable. Don't you have any other supplies houses in the area?