Table 310.15(B)(6) Service conductors Dwelling

Status
Not open for further replies.
Well thanks for the great info I tried to pass it along. I contacted the supply house and they are baffled. They told me that they carry #2 CU and that good for dwelling service, feeders ect. at 100 amps. I told the owner it won't work code does not allow it. He tells me they don't stock the SE stuff as we only stock Copper wire no Aluminum. I said you can get the stuff in copper too. He's going to continue with the same. I guess I am out of luck unless I want a big roll. That is what I get for wanting to use copper.


I had a some #2 AL SE cable out back so I used it.

Your OP was asking about #4 now you mention #2. The ampacity of 2-3 CU NM is 95 amps so as long as the calculated load is 95 amps or less it can be used for the feeder and protected with a 100 amp breaker.

I don't know much about your area but I have worked in many parts of Northern CA and every supply house I have been to has stocked AL SE cable. Don't you have any other supplies houses in the area?
 
Now it all makes more sense. I was baffled that a supply house didn't have SER!

Copper SER is a rarity, at least around here. AL SER is the norm, and nothing to be ashamed of.


My local supply house does not even have AL Se or Ser. No Aluminumm in that place.




Your OP was asking about #4 now you mention #2. The ampacity of 2-3 CU NM is 95 amps so as long as the calculated load is 95 amps or less it can be used for the feeder and protected with a 100 amp breaker.

I don't know much about your area but I have worked in many parts of Northern CA and every supply house I have been to has stocked AL SE cable. Don't you have any other supplies houses in the area?

I asked about #2 CU and placing on a 100 amp breaker and got a negative response.
 