310.15(B)(6) can not be used since you are feeding a sub-panel that does not carry "all loads that are part or associated with the dwelling unit"
Since it's an SER cable, then ampacity could be 75 amp or 90 amp depending on which Code is being enforced, where it is being installed (insulation or not) and the AHJ's mindset on 338.10(B)(4)