I would like to talk about Table 310.15(B)(6).
My question is this.
Does Table 310.15(B)(6) change the ampacity rating of the conductors or does it simply change the required OCP?
Table 310.15(B)(6) shows 400 amp OCP on 400 Kcmil copper.
Table 310.16 rates 400 kcmil 335 amps @ 75 C.
When we apply 240.4(B) to a circuit we can move up to the next standard size breaker but we can not load the cable past the 310.16 rating.
If I use 400 kcmil copper per Table 310.15(B)(6) can I load it to 400 amps?
If yes, why is that?
If yes IMO that undermines the importance of Table 310.16 and the all the derating and adjustment factors the go with it.
In my mind it can lead to this sort of statement out in the field.
"Heck the NEC overloads the conductors why shouldn't I?"
Any opinions are welcome, I can not use that table on the jobs I do, maybe I am just jealous. :roll:
Thanks in advance, Bob
[ February 08, 2005, 08:23 AM: Message edited by: iwire ]
My question is this.
Does Table 310.15(B)(6) change the ampacity rating of the conductors or does it simply change the required OCP?
Table 310.15(B)(6) shows 400 amp OCP on 400 Kcmil copper.
Table 310.16 rates 400 kcmil 335 amps @ 75 C.
When we apply 240.4(B) to a circuit we can move up to the next standard size breaker but we can not load the cable past the 310.16 rating.
If I use 400 kcmil copper per Table 310.15(B)(6) can I load it to 400 amps?
If yes, why is that?
If yes IMO that undermines the importance of Table 310.16 and the all the derating and adjustment factors the go with it.
In my mind it can lead to this sort of statement out in the field.
"Heck the NEC overloads the conductors why shouldn't I?"
Any opinions are welcome, I can not use that table on the jobs I do, maybe I am just jealous. :roll:
Thanks in advance, Bob