Ragin Cajun
Senior Member
- Location
- Upstate S.C.
This table refers to 120/240V 1 phase services. Why not also for 120/208V 1 phase??? What am I missing?
Thanks
RG
Thanks
RG
Because the neutral conductor in these systems (120/208) carries neutral current even when the load on the phases is balanced.Ragin Cajun said:This table refers to 120/240V 1 phase services. Why not also for 120/208V 1 phase??? What am I missing?
Thanks
RG
websparky said:208/120 is a 3 phase system and does not supply residential.
McDowellb said:Because the neutral conductor in these systems (120/208) carries neutral current even when the load on the phases is balanced.
I know it does. That is what i said. 120/208 VOLT. The neutral conductor carries a load even when the phases are balanced.Ragin Cajun said:Oh, but it does. Multi-family apartments/dwellings.
6-63 Log #1174 NEC-P06 Final Action: Reject
(310.15(B)(6))
____________________________________________________________
Submitter: Daniel Leaf, Seneca, SC
Recommendation: Add:
“or 120/208-volt” after “120/240-volt”.
Substantiation: Edit. This section should be applicable where dwelling units
in apartment buildings are supplied with 120/208-volt systems.
Panel Meeting Action: Reject
Panel Statement: The neutral conductor of a 120/208 volt, 3 wire system does
carry significant load. In a 120/240 volt system the load on the neutral
conductor is reduced. No substantiation was provided to justify applying the
Table to 120/208-volt service conductors.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11
Gotta agree with you here. Either way we have to account for neutral load, so why the difference? Just between us, though, a #2 copper (115A) can be protected at 125A, next standard trip rating, which happens to be the same as the table. Ditto for other sized conductors. Ohhhhh welllll. RGpaul32 said:I don't see what Table 310.15(b)(6) has to do with neutral currents. It is an allowance to use a difference size conductor for all the conductors vs. what Table 310.16 would give.