Table 310.15(B)(6)

Status
Not open for further replies.
Ragin Cajun said:
This table refers to 120/240V 1 phase services. Why not also for 120/208V 1 phase??? What am I missing?


Thanks

RG
Because the neutral conductor in these systems (120/208) carries neutral current even when the load on the phases is balanced.
 
websparky said:
208/120 is a 3 phase system and does not supply residential.

Dave, actually it can and does. I know here in the south some high rise Condo's are supplied with 120/208 wye systems which are split at the multi-gang meter equipment to single phase feeders to the individual units.

Roger
 
I agree, as Don stated many apartment buildings use a three phase, 4 wire service with single phase feeders to each apartment.
 
As Charlie once posted, the study that was conducted by the EEI which produced Table 310.15(B)(6) never submitted data on 208/120 volt systems. It appears they were not that common at the time.



Here is a proposal that was rejected for the 2008 NEC:


6-63 Log #1174 NEC-P06 Final Action: Reject
(310.15(B)(6))
____________________________________________________________
Submitter: Daniel Leaf, Seneca, SC
Recommendation: Add:
“or 120/208-volt” after “120/240-volt”.
Substantiation: Edit. This section should be applicable where dwelling units
in apartment buildings are supplied with 120/208-volt systems.
Panel Meeting Action: Reject
Panel Statement: The neutral conductor of a 120/208 volt, 3 wire system does
carry significant load. In a 120/240 volt system the load on the neutral
conductor is reduced. No substantiation was provided to justify applying the
Table to 120/208-volt service conductors.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11
 
I don't see what Table 310.15(b)(6) has to do with neutral currents. It is an allowance to use a difference size conductor for all the conductors vs. what Table 310.16 would give.
 
paul32 said:
I don't see what Table 310.15(b)(6) has to do with neutral currents. It is an allowance to use a difference size conductor for all the conductors vs. what Table 310.16 would give.
Gotta agree with you here. Either way we have to account for neutral load, so why the difference? Just between us, though, a #2 copper (115A) can be protected at 125A, next standard trip rating, which happens to be the same as the table. Ditto for other sized conductors. Ohhhhh welllll. RG
 