- Chapel Hill, NC
- Retired Electrical Contractor
I am thinking of a proposal for 2011 on this table based on the changes in 338.10. I have never done this before so I really don't have a good feel for it but I will do my best.
Here is the current wording of the table
I would like to add an asterisk after "SE" and add a note that states when SE cable is installed outdoors.
Proposed Text
It seems that currently under the 2008 SE cable is now limited to 60C when installed indoors as per article 338.10(B)(4)(a). This would mean that a 2/0 SE copper cable would be rated 145 amps and still be allowed on a 200 amp breaker. Dwellings only, of course.. It seems the intent was to lower the rating of SE but somehow I think it got overlooked in this section.
Feedback please.
Table 310.15(B)(6) Conductor Types and Sizes for 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders. Conductor Types RHH, RHW, RHW-2, THHN, THHW, THW, THW-2, THWN, THWN-2, XHHW, XHHW-2, SE, USE, USE-2.
Proposed Text
My basis is that since NM cable is not listed and rated 60C then neither should SE if installed indoors.Table 310.15(B)(6) Conductor Types and Sizes for 120/240-Volt, 3-Wire, Single-Phase Dwelling Services and Feeders. Conductor Types RHH, RHW, RHW-2, THHN, THHW, THW, THW-2, THWN, THWN-2, XHHW, XHHW-2, SE*, USE, USE-2. *when installed per article 338.10(B)(4)(b)
Feedback please.