Wwhitney the last post was respobse to you. My phone is acting up
Hopefully the 2023 NEC settles your concerns. The notes to each of the two tables correction factor tables specify which ampacity tables they may be used with. And we've explained multiple times the logic involved.Wwhitney the last post was respobse to you. My phone is acting up
Of course there are ambient temperatures that correspond to both tables. 50 deg C is both Other than 30degC and other than 40deg C.As can be seen there are ambient temperatures which may correspond to both tables.
Yes, you and David certainly have and if the OP can not understand it's pretty much futile. IMO this appears to be trolling.Hopefully the 2023 NEC settles your concerns. The notes to each of the two tables correction factor tables specify which ampacity tables they may be used with. And we've explained multiple times the logic involved.
Cheers, Wayne
I Will answer your question.Of course there are ambient temperatures that correspond to both tables. 50 deg C is both Other than 30degC and other than 40deg C.
Let's try this. According to 310.16, what ambient temperature must three #1/0 THWN copper conductors in a raceway be installed in, in order for the ampacity of those conductors to be 150?
No, I don't believe he is.Yes, you and David certainly have and if the OP can not understand it's pretty much futile. IMO this appears to be trolling.
That is brilliantNo, I don't believe he is.
Just frustration on this topic.
We have all been there on something over the years.
Jpflex
I dug the following out of IEEE Buff Book...9.5.1.3 TDF (Temperature Correction Factor.
Tn - Normal Loading Temp
Ta - Base Ambient Temp
Ta1 - New Ambient Temp
In - Normal loading current at base ambient
Ix - Current value at new ambient temp
TDF (multiplying factor) = SQRT { (Tn - Ta) / (Tn - Ta1) }
Ix = In * TDF
Play with some different cable sizes and temps and you should be able to solve for ANY ambient you encounter.
How would you solve that for final temperature, for a given load?It's equation 310.15(B) in the NEC
You're never going to get actual temperatures starting with NEC ampacity tables--the ampacity values are chosen to ensure that if all the unspecified factors are the worst plausible for heat retention, the temperature rise will not exceed the allowable rise (difference between insulation temperature limit and ambient temperature) at a current equal to the ampacity.How would you solve that for final temperature, with a given load?
We solve Ohm’s law for each variable, why not solve equation 310.15(B) for a different variable?You're never going to get actual temperatures
Sure you can do that, but the temperatures you solve for won't match what you'd get if you set up an experiment and measured the actual conductor temperature. The calculated temperature should be noticeably higher.We solve Ohm’s law for each variable, why not solve equation 310.15(B) for a different variable?
Thank IEEE…not me.That is brilliant
Can we solve for final temperature, with a given load?
Was hoping you might say that. Was I getting close in post #31 above?Yes, you can solve for conductor temp. The next section in the book goes over this.
Cannot say one way or the other.Was hoping you might say that. Was I getting close in post #31 above?
IMHO, less thermal imaging reports would follow overheated wire if more electricians paid attention to 220.18 for inductive ballast & motor loads, where current rises with voltage drop.Why does the adjusted temp interest you?
Doing that requires at least one real world temperature measurement to use as a starting point. You can not do that by calculation only just using the NEC.Yes, you can solve for conductor temp.
Only needs to avoid thermal imaging errors in violation of 110.14(C).Doing that requires at least one real world temperature measurement to use as a starting point.
Professional engineers may not want the NEC to publish such an equation, if design-build shops can use it without engineering supervision.You can not do that by calculation only just using the NEC.
30degC.I Will answer your question.
Based on this table 310.16 and what im sure you meant was the individual ampacity of 1/0 THWN with 75 deg c insulation but not the total ampacity of three paralleled 1/0 conductors in a raceway.
I understabd the ambient temp would need to be 86 degrees c. However that is not my point. What im saying is that the same ambient temperature other than 30 and 40 deg c can apply to both tables with varied results
And for those who think im trolling i just wont use table 310.15B12
That is what i said 86 deg ferenheight* or 30 deg c. However thus was not my point. My point was for ambient temperatures other than 30 and 40 which may fall into both tables. No one is getting this?30degC.
The answer is 30degC.
310.16 literally tells you that the conductors are installed in a 30degC ambient temperature.