Quick question.Under table 310.15b16 if you go to the 75 degree column. Those insulation type ampacity is rated for 75 degrees even though the actual wire size(copper or aluminum) is rated for an ampacity at 90 degrees continuous. If you are doing ampacity correction you still do ampacity correction at 75 degrees for conductors listed under this column and 90 degrees for conductors listed under the 90 degrees column , correct?