I'm sure there is an answer for this, but maybe I am overthinking. Taking a piece of copper wire, say #3 THHN / THWN. Using as THHN, this wire is good for 110 amps under the 90-degree C column. If using on a piece of equipment where the lug temperature are rated for a temp of 75 degree C, then the same wire is rated for 100 amps. However, the 75 degree column only lists this wire for 100 amps if used as THWN (as in a wet location). What if the wire is intended to be used as THHN for a dry location? What would the amperage rating be per the 75 degree column? It's almost like the THHN designation is missing from the 75 degree column. Can THHN still be good for 100A with respect to the 75 degree column? I would appreciate it if this could be explained. Thanks.