keith gigabyte
Senior Member
- Location
- New Kensington, Pa
Trying to explain to a co-worker about the table and limitations of ampacity. I am under the assumption that max ampacity is based on weakest link. If our terminations; lugs terminal blocks etc are rated at 90 deg c then we can use 75 degree c column for THHN putting #6 at 75 amps.
We will leave conduit fill de-rating out of the equation for this entire explanation
If we have 60 deg c rated lugs terminal blocks etc we use 60 deg c column even though we are using THHN wire..putting #6 ampacity at 55 amps
I am referencing 310.15 (A) informational note 1 of 2020 code
We will leave conduit fill de-rating out of the equation for this entire explanation
If we have 60 deg c rated lugs terminal blocks etc we use 60 deg c column even though we are using THHN wire..putting #6 ampacity at 55 amps
I am referencing 310.15 (A) informational note 1 of 2020 code