I'm concerned about possible damage to a 4800/120-208 volt, wye, 3phase transformer and its secondary service-lateral conductors that provide the electrical service to a strip mall by the possibility of its secondary service-lateral conductors ground-faulting or short-circuiting.
Could it be that the utility's fuses on the pole are intended to protect the primary conductors to this transformer, the transformer itself, and its secondary service-lateral conductors to the strip mall on a fault?
Does Table 450.3(A) apply for the protection of this transformer?
If it does apply, which location limitation in the table would apply, "any or supervised" and if secondary overcurrent protection is necessary, where would the overcurrent protection be placed? Would it be placed where the secondary receives its supply at the transformer or at the service disconnecting means at the building?
Thanks
Could it be that the utility's fuses on the pole are intended to protect the primary conductors to this transformer, the transformer itself, and its secondary service-lateral conductors to the strip mall on a fault?
Does Table 450.3(A) apply for the protection of this transformer?
If it does apply, which location limitation in the table would apply, "any or supervised" and if secondary overcurrent protection is necessary, where would the overcurrent protection be placed? Would it be placed where the secondary receives its supply at the transformer or at the service disconnecting means at the building?
Thanks