For a 500a main supplied with 1250kcmil Al, the building steel and watermain electrode conductor size from Table250.66 is 3/0 Cu.
For a 500a main supplied with parallel 300kcmil Al, the building steel and watermain electrode conductor size from Table250.66 is sized according to the instructions at the column heading which says, “Size of Largest Ungrounded Service-Entrance Conductor or Equivalent Area for Parallel Conductors”. The equivalent area of a double 300 is 600kcmil so the electrode conductor is 1/0 Cu.
The equivalent ampacity of a double 300 would be 1250kcmil which requires the 3/0 Cu.
Why would Table310.16 and Table250.122 and so many other parts of the code be based on ampacity and parallel conductors in Table250.66 be based on area ?
David
For a 500a main supplied with parallel 300kcmil Al, the building steel and watermain electrode conductor size from Table250.66 is sized according to the instructions at the column heading which says, “Size of Largest Ungrounded Service-Entrance Conductor or Equivalent Area for Parallel Conductors”. The equivalent area of a double 300 is 600kcmil so the electrode conductor is 1/0 Cu.
The equivalent ampacity of a double 300 would be 1250kcmil which requires the 3/0 Cu.
Why would Table310.16 and Table250.122 and so many other parts of the code be based on ampacity and parallel conductors in Table250.66 be based on area ?
David