Table (a) assumes an ambient of 30C, and gives correction factors for up to 85C, for conductor insulation systems rated up to 90C.. Table (b) assumes an ambient of 40C, and gives correction factors for up to 225C, for conductor insulation systems rated up to 250C. Both are said to have been derived from the same equation 310.15(B)(2). However, as an example, looking at the row for an ambient of 50-55C and the columns for insulation systems of 60, 75, and 90C, the tables do not show the same correction factors. So I am confused.