I interpret that as meaning, kitchen, family room, dining room, living room, parlor, library, den, sunroom, bedroom, recreation room, and any room that is similar to any of these, as well as kitchen, pantry, breakfast room, dining room, and any area that is similar to any of these, as well as kitchens, pantries, breakfast rooms, and any area that is similar to any of these, as well as bathrooms, outdoors, laundry areas, basements, garages, and hallways.That depends on how you interpret "In all areas specified in 210.52".
how about a deicated outlet for say a refrigerator? or washer? or microwave? and garage door opener or applaince garage?
Commentary: NEMA proposal 18-40 would require the use of tamper resistant receptacles throughout dwellings. The overwhelming consensus was to accept this proposal, but a considerable amount of time was spent debating whether the requirement for tamper resistant receptacles should be limited to only those that are easily accessible to children. For instance, it was questioned whether the receptacles behind refrigerators, or on walls behind counter tops, should need to comply. Panel members also questioned the ease with which attachment plugs could be inserted into tamper resistant receptacles, resulting in the writing of the following panel statement:
?The panel is concerned about the possible increased insertion force required for our aging population. The panel requests data concerning the amount of force necessary to insert a plug into the shutter and the amount of force necessary to fully insert a plug into a tamper-resistant receptacle?.
The panel finally agreed to accept the proposal without any location restrictions to see what comments were generated during the public review phase. The IAEI representative voted against the proposal. The IEC representative abstained from the voting.
Heaven forbid an NEC codemaking panel come up with something in plain English.
For crying out loud rather than leaving it for us to guess what you mean how about you just say what you mean.
I seriously think that ego plays a role in some of the things they come up with. A bunch of lawyer wannabes.
I'll give it a shot.
"All 120v receptacles installed in a dwelling unit shall be tamper resistant."
Wow that was tough.![]()
"All 120v receptacles installed in a dwelling unit shall be tamper resistant."
OK, that might workM.D. said:and I think it should read " in or associated with a dwelling unit....:smile:
But that wouldn't include receptacles on the exterior, in or on associated buildings, or elsewhere on the property.
"All 120v receptacles installed in a dwelling unit shall be tamper resistant."
:smile:
But if they said it all that simply ,.. what would debate????
There is no such thing as a 120v receptacle, they are 125v rated! Sweet, a loophole!![]()
Definition of Voltage, Nominal. Loophole closed.
You can't shut down the argument that quickly, we're only on page two. I guarantee this will be argued for at least another 4 or 5 pages.![]()
210.63 is one place that tamper resistant rec wouldn't be required if someone would want to carry both types of recs.
I only carry TR recepts now.