Assuming you mean the 2017 NEC, TR receptacles are required in: Business offices, corridors, waiting rooms, and the like in clinics, medical & dental offices & outpatient facilities.Could someone help me clarify the the new code on tamper resistant receptacles in office spaces.
I don't have the book yet and i can't find anything useful online.
Thanks!
Assuming you mean the 2017 NEC, TR receptacles are required in: Business offices, corridors, waiting rooms, and the like in clinics, medical & dental offices & outpatient facilities.
406.12(5) There are a few new others places required as well.
So the real question is, is the office space your working on relate to a clinic, medical, dental or outpatient or daycare facility or dwelling?
If not your OK with regular receptacles.
No. Under 2017 code if it's a 120V receptacle it is going to require a TR anywhere and everywhere and is no longer limited to child care areas and dwellings.So the real question is, is the office space your working on relate to a clinic, medical, dental or outpatient or daycare facility or dwelling?
If not your OK with regular receptacles.
No. Under 2017 code if it's a 120V receptacle it is going to require a TR anywhere and everywhere and is no longer limited to child care areas and dwellings.
Not quite everywhere.No. Under 2017 code if it's a 120V receptacle it is going to require a TR anywhere and everywhere and is no longer limited to child care areas and dwellings.
Still leaves a lot of places where it isn't required. But I can see many EC's putting them everywhere in dwellings, guest rooms, child care, schools, medical facilities as a general rule just to avoid missing some that should have been TR. Re-inspections may cost more then just using the TR receptacles to begin with.Not quite everywhere.
406.12TR Receptacles
Dwelling units in all areas specified in 210.52 and 550.13
Guest rooms and guest suites of hotels and motels
Child care facilities Preschools and elementary education facilities
Business offices, corridors, waiting rooms and the like in clinics, medical and dental officesand outpatient facilities
Subset of assembly occupancies described in Article 518.2 to include places of waitingtransportation, gymnasiums, skating rinks, and auditoriums
Dormitories
Informational Note: This requirement would include receptaclesidentified as 5-15, 5-20, 6-15, and 6-20 in ANSI/NEMA WD 6-2016, WiringDevices — Dimensional Specifications.
Exception to (1), (2), (3), (4), (5), (6), and (7): Receptacles in the followinglocations shall not be required to be tamper resistant:
Receptacles located more than 1.7 m (5 1⁄2 ft) above the floor
Receptacles that are part of a luminaire or appliance
A single receptacle or a duplex receptacle for two appliances located within the dedicatedspace for each appliance that, in normal use, is not easily moved from one place to anotherand that is cord-and-plug-connected in accordance with 400.10(A)(6), (A)(7), or (A)(8)
Nongrounding receptacles used for replacements as permitted in 406.4(D)(2)(a)
The first part of his text is where they are required now, the exceptions very limited.Still leaves a lot of places where it isn't required. But I can see many EC's putting them everywhere in dwellings, guest rooms, child care, schools, medical facilities as a general rule just to avoid missing some that should have been TR. Re-inspections may cost more then just using the TR receptacles to begin with.
Did he quote 2014? I have no idea what is in 2017 yet. I can see this eventually going to where it is required in enough places that many EC's won't install anything else just to avoid code violations.The first part of his text is where they are required now, the exceptions very limited.
That was from the 2017 NEC.Did he quote 2014? I have no idea what is in 2017 yet. I can see this eventually going to where it is required in enough places that many EC's won't install anything else just to avoid code violations.
I thought it probably was.That was from the 2017 NEC.
I sort of agree with you. But look at how many other things are out there (not just in the electrical field) that we are forced to use in the name of safety or environmental hazards whether we want those features or not. How much less would today's automobiles cost if we didn't have all the safety features and environmental conservation features mandated on all these vehicles? Then there is the maintenance of such features that sometimes becomes necessary.I think this is nuts. More manufacturers just trying to make people buy their products.
Some areas I can see, but dorms? Doesn't that include college dorms? Aren't college kids old enough to know better than to stick a paper clip in a receptacle?
In the past, a receptacle would easily last 50 years if it wasn't abused.
I have one TR receptacle in my house. After about 1 year, most plugs won't unlatch it anymore. Now I keep a 2 prong adapter plugged into it because it works for some reason. But anything with a ground pin is no longer grounded. And when these things quit working people are going to start using extension cords from the closest outlet instead of paying someone $100 to replace a $5 outlet.
My point is these aren't going to be any safer if they aren't reliable.
It will be lots of easy service calls for electricians.
Some areas I can see, but dorms? Doesn't that include college dorms? Aren't college kids old enough to know better than to stick a paper clip in a receptacle?
We can send them off to find out anything they haven't already learned in high school about drugs, alcohol, sex, and just lifestyle choices in general, but we can't trust them to keep paper clips out of the power receptaclesAs someone who worked at a college for 10 years I can state with no hesitation: For the most part - No. A complete lack of common sense is prevalent among many, if not most, of our young students in higher academia. Sad, but true.
It’s all about money more mouths to feed more people to come up with more stuff more people to do something stupid but oh it can happen so we all buy in and it gets added on and piled on.I sort of agree with you. But look at how many other things are out there (not just in the electrical field) that we are forced to use in the name of safety or environmental hazards whether we want those features or not. How much less would today's automobiles cost if we didn't have all the safety features and environmental conservation features mandated on all these vehicles? Then there is the maintenance of such features that sometimes becomes necessary.
Not saying all those features are bad, but when buying a new vehicle we don't have a choice either, they will have certain features included, some which used to be optional are now required. In the future some of the options today may be required.
Having big brother watch out for you does have a cost.