A question came up on an inspection: Do the receptacles located inside the medicine cabinet have to be tamper resistant [medicine cabinet came with the receptacles already installed (and listed) by the mfr.]?
406.11 refers us to the receptacles required in 210.52 => 210.52(D) makes a requirement for at least one receptacle installed within 3' of the outside edge of each basin [2008 NEC].
As an inspector my response was: 'Since you have met the requirement of 210.52(D), I don't believe those receptacles inside the cabinet must meet the TR requirement.' [i.e. 'go for it.']:thumbsdown:
Now you can bash me for being a softy.
406.11 refers us to the receptacles required in 210.52 => 210.52(D) makes a requirement for at least one receptacle installed within 3' of the outside edge of each basin [2008 NEC].
As an inspector my response was: 'Since you have met the requirement of 210.52(D), I don't believe those receptacles inside the cabinet must meet the TR requirement.' [i.e. 'go for it.']:thumbsdown:
Now you can bash me for being a softy.