Re: TANDEM OR CHEATER BREAKERS
Ryan
CL type tandem breakers are the only listed breakers that can be installed in a CL type panel. and you know when you have a CL type panel by the 200MB 30/40 model #. but before they devoleped CL type panel's they still allowed tandems in panels that was listed for them but they didn't have the rejection tab. and since these panels are still in use they are allowed to be repaired when these breaker's go bad. so the Non-CL type tandem's are only allowed to be installed in the older Non-CL type panels as replacement's only. If they are found in a newer CL panels it is a violation of listing. 110.3(A)(7)
As for the other note In a CL panel the tandems are only allowed to be installed in the spaces provided for them. No where else.
iniskea
The code section that you are looking for is:408.15