Plus, they lime up pretty quickly unless you're running a water softener.A large tankless electric water heater can draw this much. IMHO a stupid way to use electricity.
Jon
Plus, they lime up pretty quickly unless you're running a water softener.A large tankless electric water heater can draw this much. IMHO a stupid way to use electricity.
Jon
NoIs it safe to assume that would be 11,520 VA? '
Most furnaces have a label, somewhere.I have been working on a load calculation for this condo. There is an electric furnace on a 60 amp breaker. Is it safe to assume that would be 11,520 VA? 60 amps x .80=48 x 240= 11,520. '
Probably close enough for a load calculation.I have been working on a load calculation for this condo. There is an electric furnace on a 60 amp breaker. Is it safe to assume that would be 11,520 VA? 60 amps x .80=48 x 240= 11,520. '
A majority of heat strips that are called 10 kW typically has actual heat capacity of 9.6 kW of heat. If there is blower on same circuit it is usually no more than about 2 amps.I have been working on a load calculation for this condo. There is an electric furnace on a 60 amp breaker. Is it safe to assume that would be 11,520 VA? 60 amps x .80=48 x 240= 11,520. '