LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
I am about to install a couple of tankless water heaters. Not the kitchen-sink Insta-hot, but the whole-house, no-storage-tank kind, that supposedly meets continuous demand. Of course, anyone could leave a hot faucet open, but...
One was on site, the other one is on the way. The one I saw was rated at 28Kw, divided into four 7Kw (29.2a) feeds. I did a forum search with the word "tankless" and found just enough info to not quite answer my questions, so here goes:
1) Is a tankless water heater considered to be a continuous or non-continuous load? That will make the difference between #10 on 30a breakers and #8 on 40a breakers.
2) To what degree do load calcs apply to existing installations as it does in new work? This new load (116.8a) may require a 200-to-400 (320, actually) service upgrade.
3) The customer wants me to wait to see if he has main-breaker tripping problems before he's forced to commit to a service upgrade. Is that okay to agree to, or must we not even approach the possibility?
All replies appreciated!
One was on site, the other one is on the way. The one I saw was rated at 28Kw, divided into four 7Kw (29.2a) feeds. I did a forum search with the word "tankless" and found just enough info to not quite answer my questions, so here goes:
1) Is a tankless water heater considered to be a continuous or non-continuous load? That will make the difference between #10 on 30a breakers and #8 on 40a breakers.
2) To what degree do load calcs apply to existing installations as it does in new work? This new load (116.8a) may require a 200-to-400 (320, actually) service upgrade.
3) The customer wants me to wait to see if he has main-breaker tripping problems before he's forced to commit to a service upgrade. Is that okay to agree to, or must we not even approach the possibility?
All replies appreciated!