I got a call to look at a problem for a tanning bed intermittantly tripping its breaker on start up.
Its a commercial 3 phase bed, wired by the installer to run on 240v single phase. They installed a buck boost and the measured voltage is 238v on the secondary. Data sheet shows it 50 amps. Measured current is 61 amps.
I called the supplier/installer and was told that current is perfectly normal when wired like it is.
All of this is wired with #4 cu on a 70 amp QO breaker. The intermittent trip occurs when the
"Start" is pushed on the bed.
The installer is saying the breaker must be bad. I think the breaker needs to be larger.
Again its intermittent, ONLY on startup, not once its running. I'll attempt to post pics but it says file too large.
Anyone run in to this before?
Its a commercial 3 phase bed, wired by the installer to run on 240v single phase. They installed a buck boost and the measured voltage is 238v on the secondary. Data sheet shows it 50 amps. Measured current is 61 amps.
I called the supplier/installer and was told that current is perfectly normal when wired like it is.
All of this is wired with #4 cu on a 70 amp QO breaker. The intermittent trip occurs when the
"Start" is pushed on the bed.
The installer is saying the breaker must be bad. I think the breaker needs to be larger.
Again its intermittent, ONLY on startup, not once its running. I'll attempt to post pics but it says file too large.
Anyone run in to this before?