D Designer69 Senior Member Sep 19, 2017 #1 Just want to make sure this works and there's nothing wrong with it. The blue cable would be new. Sanity check. thank you Last edited: Sep 19, 2017
Just want to make sure this works and there's nothing wrong with it. The blue cable would be new. Sanity check. thank you
J Jim1959 Senior Member Location Longmont, CO Sep 19, 2017 #2 Designer69 said: View attachment 18534 Just want to make sure this works and there's nothing wrong with it. The blue cable would be new. Sanity check. thank you Click to expand... The code doesn't allow you to put a load on a grounding conductor, only on a grounded conductor (neutral).
Designer69 said: View attachment 18534 Just want to make sure this works and there's nothing wrong with it. The blue cable would be new. Sanity check. thank you Click to expand... The code doesn't allow you to put a load on a grounding conductor, only on a grounded conductor (neutral).
J JFletcher Senior Member Location Williamsburg, VA Sep 19, 2017 #3 You also cannot have the hot and neutral taking separate paths back to the panel ala K&T.
D drktmplr12 Senior Member Location South Florida Occupation Electrical Engineer Sep 19, 2017 #4 Will it work? Yes Does it comply with NEC? No, see 300.3(B)