500 kcmil tap conductors have an ampacity of 380 amps and cannot be used to terminate in a 400 amp OCPD. They would need to be increased to 600 kcmil or terminate in a 350 amp OCPD.We are using 500 kcmil THHN conductors, which are suitable for a 400A breaker.
Note tap conductors are one of the situations where you cannot use the "next size up" ruleThanks. We have checked and confirmed that the existing service can handle the load. We are using 500 kcmil THHN conductors, which are suitable for a 400A breaker.
If they eliminated the tap they could use 500 kcmil without the 400 amp OCPD.Note tap conductors are one of the situations where you cannot use the "next size up" rule
Yes. That is fine.Can we tap a 400A main electrical service board with a new 400A breaker to feed temp load? See attacehd SLD. Thanks for your guidance in this matter.