I've used the Kup-L-Taps, most recently for a fire-suppression system up-grade in a deli kitchen in a large grocery store. Their biggest benefits are simple installation and hot installation (unloaded.)
The entire kitchen panel is shut off by a shunt-trip main breaker, which was great and convenient for me, except that the exhaust fans and horn-strobe need power during a system trip.
So I tapped off of the incoming 500mcm conductors with #4's, using Ilsco IPC-500-250's, which are rated for 250 to 500mcm's on the run, and #4 to 250mcm's on the tap. Didn't even need to kill the power.
I ran the #4's to an 8-space panel, landing them on a back-fed (and secured) 60a breaker, and two 20a breakers for the two exhaust fans, and a 15a for the contactor power and the horn-strobe.
This does lead me to a question of my own: within the 10-ft tap rules, must the tap land on a single OCPD, like I did, or can the 6-handle rule be applied here? I can't tell for sure reading 240.21(B)(1).