To be honest, this is wiring from secondary of a utility xfmr, the power company does not provide us the larger xfmr that we wanted. So, on secondary of their xfmr they will run a wireway -36" long hold (4) 3/0 copper to our tap box and from output of this tap box, we run (4) 4"C - each conduit has 600kCM to our main gear inside the building.
I assume we will have (2) rows of (2) 4" conduits come out of tap box, starigh run to the main gear.
Consultant credit card because of sizing wrong tap box???....That's why we need to blame on electrician to size and install the box (-: