Here's the set up. Coming from the poco I have a set of Secs that land right in a combination type trans-s with built in disconnect all in one enclosure. The SECS hit the switch first rated 600a this is fed via 2sets of 350 mcm
Coming off the switch we have double lugs
And ran a set of 500s to two different main lug panels
Is this compliant?
Is this considered a tap?
If we landed the 500s to a 400a main breaker would it then be compliant ? I say yes
Also I suggested to just change the main fuse to 400a protecting the 500s Wich in my opinion is fine?
Am I wrong for thinking potentially the 500s could be overloaded because there is the main 600a fuse?
I know that tap rules don't apply to service conductors but after the main switch these are no longer service conductors so I guess my question is . Isa double lug considerd a tap?