It seems you're standing on this by yourself. That's fine.

The whole mass of humanity (actually just 5 or 6 electricians or EEs), is on the other side of this one, but that's OK, too.
110.14(C)(1)(a) says the termination provisions apply to all the terminations on the circuit:
"Termination provisions of equipment
for circuits rated 100 amperes or less, or marked for 14 AWG through 1 AWG, shall be used
only for one of the following:"
You are trying to mix the flavors, that is, use two of the options on one circuit. As I read it, NEC says no.
But that's OK. We disagree. As Smart says, we could keep going, but I don't suppose we need to.