I have 208/120V 400 amps fused service disco inside building incoming line side 4#500 kcmil service conductors. Load side of the service disco lug I have conductor A 4#3/0 + #3/0G to Panel A and at same point load side of service disco lug I have conductor B 4#3/0 + 3/0G to Panel B.
I would be assuming Conductor A is tap conductor so is conductor B but these are not feeder taps as their is no feeder being tap both are connected at single point load side lugs of service disco. So what tap conductor rules apply for conductors A and B in code?