tap conductors nonfuse to condensor

Status
Not open for further replies.

howardrichman

Senior Member
If I'm to use larger (10GU) feeder to an A/C condensor, then use 12 conductor wire from the disconnect to a A/C condensor; is that allowable w/o fusing the whip to the condensor w/20A fuses if I'm using a 20A HACR breaker feeding the #10 feeder? Does a tap rule apply in this case. There is to be an inspection.

Thanks;
HR...
 
If you are protecting the circuit with a 20 amp breaker at the supply end, then the #12 would be fine as it is protected,
Just for discussions sake, do you know the Minimum Circuit Amps and the Maximum Overcurrent Protection values for the unit ??
 
Last edited:
Hopefully, the unit is marked to accept HACR breakers also and not just "fuse". If so you are fine.
Think of the set-up as one installed for voltage drop. On over sized conductor for a portion of the run then reduced to the "normal" ampacity conductor for another portion.
 