Look at 215.2(A)(1) ...210.19(A)(1) also for grins and giggles.This paragraph?
That seems to say the same thing as 110.14(C), that conductors with an insulation temperature rating higher than the temperature rating of the terminations can take advantage of the higher ampacity for correction and adjustment factors, but that the ampacity is still limited by the tabular value for the temperature rating of the terminations.
That's bridge under the water.This thread's a blank slate as far as I'm concerned.
I've always been a bit unclear on whether an installed conductor has a single ampacity, or whether it has different ampacities for different purposes, or what, so I would welcome any references you have on the topic.
Cheers, Wayne
Note the two-part determination of (a) and (b) thereunder. Part (a) is selection and coordination with 110.14(C). Part (b) is selection and coordination with 310.15(B) second paragraph of general statement.
I'm saying all that is necessary to comply with 240.21(B)(2)(1) is a part (b) determination. Actual circuit ampacity will have to comply with a full determination using 215.2(A)(1) parts (a) and (b).
Revisit the problem posed in the OP. 400A feeder mentioned so we will assume a 400A OCPD rating, as a 240.21(B)(2)(1) determination is based on OCPD rating not feeder conductor ampacity. To qualify, the tap conductor ampacity must be at least 1/3 of 400A or 133A.
#1 copper is rated 145A @ 90°C but only 130A @ 75°C. Let's say our load is not more than 125A noncontinuous or 100A continuous so we can use a 125A-rated OCPD and 75° terminations. Can you explain why OP'er cannot "safely" use #1 rather than going with #1/0?