Tap or Service?

Status
Not open for further replies.

JoeNorm

Senior Member
Location
WA
Hi all,

Trying to clear my head a little. I have familiarized myself with feeder tap rules to a reasonable degree. As "feeder" taps they only apply after the first means of disconnect. Anything upstream would be on the utility side.

Are there "tap" rules for the utility side, or do we just apply the rules of services here? Can conductors of reduced size(like a tap) be connected to service entrance conductors?

Thanks
 
Would you be allowed to attach a smaller gauge wire onto a larger gauge wire like you can with a tap? I do not have my code book handy at the moment.
 
Would you be allowed to attach a smaller gauge wire onto a larger gauge wire like you can with a tap? I do not have my code book handy at the moment.
Yup, as long as the service overcurrent device has a setting of the smallest conductor (service conductors that serve multiple service disconnects can be sized to the load not the sum of the OCPD's). 230.90(A) and exception #3.
 