I think that IPC's are designed to establish connections without shutting down. Solar Pro (the magazine) thinks so, too.[/B]
There is virtually no case where hot work rules would allow this.
I think that IPC's are designed to establish connections without shutting down. Solar Pro (the magazine) thinks so, too.[/B]
I know for a fact that it (installing IPC's on the line side without shutting down the service) is a common practice in PV installations.There is virtually no case where hot work rules would allow this.
Being a common practice does not make it a safe practice.I know for a fact that it (installing IPC's on the line side without shutting down the service) is a common practice in PV installations.
No. You are asking for trouble by doing this. Anytime there are parallel conductors, you have to preserve the symmetry as much as possible.
I made a graphic illustrating the problem with only tapping onto one of the parallel conductors. Problem: calculate the current in R1, R1', and R2, given the resistances and the voltages V1, V2, and the current IPV. This represents a long feeder that is made up of parallel 250 kcmils with a 2% voltage drop across the source feeder. The PV is tapped very close to the load on set #1 of that feeder.
Do you exceed the ampacity of the 250 kcmil wire, in any portion of it?
View attachment 15420
The proper way to do this, is with a 5-terminal insulated tap connector, that has an input and output port for both wires in the existing parallel set, and then a 5th port for the PV. Or any other method that allows you to connect onto both existing conductors. A nice way to do this, is when you have an unused lug position on the existing breaker.
How about a 3 terminal insulated tap connector with an input for the pv circuit and two outputs to feed the parallel set with IP connectors?
...
The proper way to do this, is with a 5-terminal insulated tap connector, that has an input and output port for both wires in the existing parallel set, and then a 5th port for the PV. Or any other method that allows you to connect onto both existing conductors. A nice way to do this, is when you have an unused lug position on the existing breaker.
How about a 3 terminal insulated tap connector with an input for the pv circuit and two outputs to feed the parallel set with IP connectors?
I believe his question is regarding the use of a 3-conductor IPC, which electrically is no different than a "5-terminal insulated tap connector" that requires cutting the two paralleled conductors.The issue there, is that you would be terminating your "tap conductors" in to something other than an overcurrent protection device. If 240.21(B) applies in the application, this would not be permitted. It would be making a tap from a tap.