- Illinois
- retired electrician
deputygrsmith,
			That is exactly what the code requires.Once I select the proper wire size, do I take the wire's max ampacity per 310.16 and size the OCPD to either equal or less than it's max ampacity?
You are correct, the book is wrong. The wire can be protected at 150 amps. Note I am assuming that the wire is 75?C wire as that is the only way a 1/0 is large enough to satisfy the 1/3 part of the rule.If this is true, then 400a(1/3) = 133a and is a #1/0 which it's max ampacity is 150a and I should be able to use the standard OCPD of 150a? I should not have to use 125a OCPD as the book states, correct?
You can't believe everything you read in books, or even everything that you read on this forum. :twisted:The book is applying different answers and is not consistent in it's calculations and the inconsistentcy is throwing me off.