What do you do when running a feeder to serve a very large HP fire pump with a small jockey pump where the jockey pump conductors are tapped from this feeder? For instance, if you have a 2000 amp OCPD and you need to tap this feeder to serve the jockey pump, you would then need 200 amp tap conductors just to serve a 3 HP jockey pump assuming <10'?