Parallel 3/0 would be fine (assuming separate conduits.)I'm going to assume also that you can't not use two sets of 3/0 in this situation because the 3/0 ampacity isnles then 1/3 of 1200.
Or at that point are parallel feeders considered one conductor
Sent from my SM-G986U using Tapatalk
Because the ampacity would be less than 400...using the adjustment factors for more than three current carrying conductors in a raceway.Why would I not be able to run in the same conduit
Sent from my SM-G986U using Tapatalk
YesIf you were to run 4 sets of 500kcmik off of a 1200 ocpd and terminated into 4 separate panels would they still be considered a tap
Sent from my SM-G986U using Tapatalk
Yes, that is a feeder and you can use the feeder tap rules. You can't tap just one set of the conductors, however. You could use something like polaris multitap blocks to make the tap, or maybe you can add an additional lug to the bus in the meter bank tap box. The tap conductor ampacity must meet or exceed the rating of the main c/b on the standalone meter stack section.Its an interesting modification for sure
petersonra's earlier reply - "is it a tap or not" referrers to the actual definition of the conductors ? from the existing building main to the existing meter stack tap box (about 12' up over and down, away) via 3 sets of 90s on each side - i see these as feeders
I conclude yes we can employ a tap rule here , as we are not planning/hoping to extend all 3 sets of feeders from one meter section tap box to another
and if they terminate on a main cb for the stand alone new meter stack section then our one set of conductors should be protected ?
Bob
The only thing I may disagree on is the last sentence. If the meter stack section was "main lug". In that case it seems the wording in 240.21(B)(1)(1)(b) would allow it (Although the tap ampacity would need to be greater than that of the meter stack which would likely make it just a feeder continuation in practice).Yes, that is a feeder and you can use the feeder tap rules. You can't tap just one set of the conductors, however. You could use something like polaris multitap blocks to make the tap, or maybe you can add an additional lug to the bus in the meter bank tap box. The tap conductor ampacity must meet or exceed the rating of the main c/b on the standalone meter stack section.
I'm not sure I follow. Maybe you missed that the OP said he would be terminating on a main c/b?The only thing I may disagree on is the last sentence. If the meter stack section was "main lug". In that case it seems the wording in 240.21(B)(1)(1)(b) would allow it (Although the tap ampacity would need to be greater than that of the meter stack which would likely make it just a feeder continuation in practice).
I don't believe he said that. I believe the question was does he need over current protection.I'm not sure I follow. Maybe you missed that the OP said he would be terminating on a main c/b?
I don't believe he said that. I believe the question was does he need over current protection.
I conclude yes we can employ a tap rule here , as we are not planning/hoping to extend all 3 sets of feeders from one meter section tap box to another
and if they terminate on a main cb for the stand alone new meter stack section then our one set of conductors should be protected ?
Ok well that is not the OP, but irregardless (not a word), as an academic question, what are your thoughts about that wording and it's intent in 240.21(B)(1)(1)(b)?He seems to be saying the tap will terminate on a main c/b to me.
Ok well that is not the OP, but irregardless (not a word),
as an academic question, what are your thoughts about that wording and it's intent in 240.21(B)(1)(1)(b)?
Nice! I'm going to have to try and use that sometime.I think you mean disirregardless (actually heard someone say that once)
Ok I had to read that several times, its kinda confusing with the "or" and the double negative. I think you are saying the tap must terminate on an OCPD. IF so, how do you interpret the part in red? Couldnt that "device" be something like a meter stack? If not, what is this "device" they speak of and why the different language than in the 25' tap rule?See post #7
Not less than the rating of the equipment containing
an overcurrent device(s) supplied by the tap conductors
or not less than the rating of the overcurrent
protective device at the termination of the tap conductors.