I don't see why not, what code section would you cite? There is a potential issue on how exactly the tap is made if there are not existing lugs available. The AHJ may have the right to request a field evaluation. See this document (may be specific to switchboards I can't remember).
I don't see why not either, and, I'm no looking to cite any code.
I was Just trying to get clarity in my head the rule if you do decide to tap.
I started thinking of the 25' tap which requires the tap to land on an overcurrent protection device first.
On a group metering tap from the buss bars to a combo meter main, the tap would not land on the overcurrent protection first. It would land on the line side terminals of the meter in the combo first.
That's what prompted my question of a NF disconnect being allowed to be in line prior to the overcurrent protection since it mimics the line and load tabs on the meter to a tenant main as a tap splice.
If the first landing point of the feeder tap had to be the OCPD, and, Not a terminal block or anything in between, then, you couldn't use the 25' tap rule at all.
Then, we're down to a 10' tap rule which is much more forgiving.
That rule indicates "not less than the rating of the device supplied by the tap conductors or the OCPD "
at the termination of the tap conductors".
My question then was can there be anything between the tap at the group metering buss and the overcurrent protection device located in the combo meter/main your feeding.
If you consider the tap conductor has not been altered by running it through a terminal block, NF disconnect, or, Tabs on the meter, then, nothing about the rule would prohibit you from doing so.
Those points would simply be an extension of the tap conductor.
In short I say, Tap it.
As others have said the only determination is whether your dealing with Service Conductors or Feeder Conductors, which I've now discovered they are Feeder conductors on the load side of the OCPD in a group metering setup, whereas before I was at the understanding that in a group metering setup they were actually service conductors all the way to the line side of the meter bases.
I learn something new here every day and appreciate it.
Thanks,
Jap>