So no need for any breakers in the 2 panels? Just the breaker in DP panel that feeds the 2 panels ? Didn't seem right to me . But thanks for the help.
It's the word "Tap" that throws most people off.
It's very common to hear, "We're gonna tap off of that and go to there" or " Then we're gonna go tap a keg when we get done".
The word "Tap" itself only means that your going to connect something to something.
In electrical, you have to look at it as a 2 step process.
Yes, they did "Tap" off of the 1st panel to feed the 2nd one by connecting the wires going to the 2nd panel to the wires feeding the 1st panel, but, they did not decrease the size of the conductor to the 2nd panel.
In that case, the Overcurrent protection device feeding the 1st panel will protect the wiring to the 2nd panel because they are both the same size conductors.
Now.
If they had of reduced the size of the wire from where they made the tap to the 1st panel to the 2nd, then, that would have actually been a tap because the overcurrent device protecting the wire to the 1st panel would have been larger than what the smaller wire to the 2nd panel was designed to carry
That's when the actual "Tap Rules" come into play, and, there are different rules depending on the type of tap, and, how far those smaller conductors travel
before landing on some type of protection themselves.